17-Apr-2010 - 151 Front Annual Building Shutdown

Announcements concerning Networking & Related News, Planned Outages, Anything which may affect your services.

Moderator: Admins

Post Reply
porcupine
Site Admin
Posts: 704
Joined: Wed Jun 12, 2002 5:57 pm
Location: Toronto, Ontario
Contact:

17-Apr-2010 - 151 Front Annual Building Shutdown

Post by porcupine »

Hello Everyone,

Please be advised of the following maintenance window:

Maintenance Window: Saturday April 17th, 2010, 8:00AM EST - 7:00PM EST

Affected Device: Primary power feeds
Affected Customers: All customers
Service Impacting: No - Precautionary maintenance notice

Details: This maintenance notice is being issued with regards to the annual 151 Front St. W. building hydro shut-down that is scheduled for 17-Apr-2010, with a maintenance window from 8:00AM EST until 7:00PM EST.

Once a year, 151 Front St. W. shuts down all of its utility power, and removes itself from the commercial power grid in order to perform extensive annual preventative maintenance on its core power infrastructure. During this time, all tenants within the building operate off their existing diesel generator/alternate power sources.

While customers should see no direct impact to their core services as a result of this maintenance period, we are issuing this as a precautionary notice, as extensive work is being done to building infrastructure with relation to the power systems.

Cabinet colocation customers should be aware of the following:
- Priority Colo staff will be retained on-site for the duration of this maintenance as a precautionary measure, and will be happy to help with any concerns (as always).
- Full unescorted access will be available as per normal; however customers can expect delays in signing in at the front desk, and signing in guests.
- Noise levels in the 818 suite will be elevated due to the operating generators on the mechanical suite above. Hearing protection (earplugs) will be provided as necessary.

For interested customers, a rough series of events is as follows:
- The building generator we reside upon will start, and be made available to our suite (our ATS will see both generator and utility power present).
- Our ATS will transfer its load from commercial power, to the generator. Our Air Conditioning units will reset (as they are not powered by UPS, by design).
- Utility power will remain available for ~30 minutes, to ensure there are no initial problems with the generator we reside upon.
- The building will shut down its core utility power, and perform infrastructure maintenance
- Utility power will be restored upon the completion of this maintenance.
- Our ATS will see both generator and utility power sources available, and transfer to utility power. Our Air Conditioning units will reset (as before).
- The generator will continue to run for ~30 minutes to cool down (and in case of post-maintenance utility failure).
- Maintenance window will be closed.


Customers who have any questions, or concerns with regards to this maintenance should contact me directly ( myles@prioritycolo.com ) for additional details.
Myles Loosley-Millman
Priority Colo Inc.
myles@prioritycolo.com
http://www.prioritycolo.com
porcupine
Site Admin
Posts: 704
Joined: Wed Jun 12, 2002 5:57 pm
Location: Toronto, Ontario
Contact:

Re: 17-Apr-2010 - 151 Front Annual Building Shutdown

Post by porcupine »

We have just received word that building management has revised the maintenance schedule. The new schedule is as follows:

Maintenance Window: Saturday April 17th, 2010, 7:00AM EST - 7:00PM EST

My apologies for the short notice, unfortunately the schedule was revised at the last minute (pushed ahead by over an hour) by building management.
Myles Loosley-Millman
Priority Colo Inc.
myles@prioritycolo.com
http://www.prioritycolo.com
porcupine
Site Admin
Posts: 704
Joined: Wed Jun 12, 2002 5:57 pm
Location: Toronto, Ontario
Contact:

Re: 17-Apr-2010 - 151 Front Annual Building Shutdown

Post by porcupine »

Hi guys,

This maintenance period is now closed. The annual building shutdown has come to an end without any incidents, everything has gone smoothly as anticipated.
Myles Loosley-Millman
Priority Colo Inc.
myles@prioritycolo.com
http://www.prioritycolo.com
Post Reply